Generac XG8000E only producing 67volts on each leg.
Beware of an adjustment complexity with an new kind of poweroutlet automatic voltage regulator avr , have you measured the generator UNLOADED for 230 volts ?
because it can be normal that 67 volts output changed when you connect an paint heat gun i was surprised a few weeks ago that i get an GENMAC 8000 that is a look a like generator coming from china build . first i was measuring some of the same output AC instead of 230volts.
6/28/2019 10:45:06 AM •
Generac...
•
Answered
on Jun 28, 2019
Generac 14kw Lp mod 0055030 ser 5437842
Battery was dead. Replaced but has code RPM SENSE LOSS.
RPM Sensor Loss 1501
ALARM
This RPM alarm is set when a 2 cylinder unit was already running and stalled or lost the RPM signal from the ignition coils. Possible causes could be a fuel issue, the LP tank is empty, 1 or both ignition coils are damaged, or the unit was overloaded quick enough that the engine stalled and set the alarm.
Possibly a fuel flow issue.
Try running without load for awhile, if it faults with no load then either an ignition module or control board or fuel. If it only faults with significant load, then more likely a fuel flow or engine is stalling from sudden increase in load.
6/3/2019 8:40:38 PM •
Generac...
•
Answered
on Jun 03, 2019
Can Code 1902 for a Generac 8KW be fixed by the owner?
If you have some fundamental electrical training/experience.
Undervoltage 1902
ALARM
Fault is displayed when both zero crosses are missing from the controller's input for 1.5 seconds or more. Could be a faulty excitation winding, zero cross circuit, loose wiring, or field boost hardware problem. Same applies here, v1.12 or later firmware should be installed.
6/2/2019 8:55:03 PM •
Generac...
•
Answered
on Jun 02, 2019
I have a propane 20 KW Generac showing in that displays checksum failed
Embedded processor memory error. The genset processor runs a periodic sum of all instruction memory space and compares it to a known value "check sum". Your unit has failed this test which means processor instruction space is potentially corrupted. This is a fatal error and it will not allow the genset to run until it is corrected. Likely this will require replacing the control board.
3/18/2019 8:57:29 PM •
Generac...
•
Answered
on Mar 18, 2019
I have a standby Generac generator that keeps blowing the 15A fuse. What can cause this to happen?
Does the fuse holder or wiring diagram have the fuse size listed on it ? It could be an incorrect fuse size from the factory or installed by someone who was just lucky the day they installed it and it ran with what is essentially a fuse with too low a rating.
Are you using the correct voltage rating ie 120volts not 12volts or whatever.
IF IF the second fuse works that kinda tells me there is no fatal short in the system, otherwise it would blow that fuse also.
I would try a 20amp or a 17.5amp if it's made in the configuration you need. Preferably the 17.5.
If you replace the 15A with the 20A and it blows then you have a problem.