When temp is below freezing furnace will not ignite. Fan will turn on but there's no combustion. eventually it kicks on but shuts down after a few min. We only have this problem in the really cold temps.

2 Answers

Brian Mills

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

  • Master 613 Answers
  • Posted on Jul 11, 2014
Brian Mills
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

Joined: Aug 22, 2013
Answers
613
Questions
0
Helped
133257
Points
1126

Is this a propane or natural gas furnace ?

Anonymous

Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

New Friend:

An expert that has 1 follower.

Hot-Shot:

An expert who has answered 20 questions.

  • Contributor 59 Answers
  • Posted on Jan 29, 2011
Anonymous
Contributor
Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

New Friend:

An expert that has 1 follower.

Hot-Shot:

An expert who has answered 20 questions.

Joined: Dec 12, 2010
Answers
59
Questions
0
Helped
15153
Points
96

Check the condensate drain lines in the furnace. disconnect the power and remove the cover. Remove the black drain lines and flush and clean with a water and clorox solution. Then check the rest of your condensate drain line for blockage. the blockage is freezing and causing the furnace to shut down for a pressure problem.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

My good man furnace model gmh80903bnca will not get to temp fan shuts off and burners keep burning then kicks off on high limit then starts process over but never gets to temp set at 655

If you have a switch that can manually turn on the fan, try it to verify the fan works. This is what I think is happening. The normal operation should be thermostat calls for heat, inducer fan comes on, pressure switch closes, igniter glows, main burner ignites and then in 30 or so seconds the fan comes on and stays on until the thermostat is satisfied. Once the thermostat is satisfied the burner shuts off and the fan runs for approx 120 seconds then shuts off. I think the control board that automatically turns your fan on is faulty. On most modern furnaces if the auto fan control fails and the furnace gets to hot and limits, when the limit opens and shuts off the burner it also energizes the fan motor to cool the heat exchanger.
2helpful
3answers

Trouble shoot Dayton gas furnace model GG9S100C16MP11A fan is left on constant but in cold weather 10 or colder fan will go off and furnace will go thru a restart mode and run fine for awhile then will do...

Do not run contentiously during heat mode. the fan runs at a slower speed with heat and heat fires first then the fan cycles on during heat cycle then when heat satisfies the thermostat the heat will cycle off and fan will run for a couple more minutes and then cycle off. So set stat on fan cycle to auto.
0helpful
1answer

I have a Braeburn 3200 and when the the temperature reaches the desired heat setting. The furnaces heat will shut off, but the fan will continue to run indefinetly. eventually blowing very cold air up

The fan relay is stuck in the on position. When the temperature drops the heater does not ignite because the fan is already running and ignition is locked out after the heat cycle starts an the fan turns on
0helpful
1answer

Can i hook up a thermostat to my hot blast wood/coal stove to control the heat in my home

Yes, you most certainly can. It depends on how handy you are and to what extent you are willing to go to make this happen. A lot will depend on how comfortable you are with electrical wiring and understanding HVAC controls and their function.

First though, this is the typical way a wood fired forced air furnace is designed to operate. There is a control transformer and relay to control either a combustion air fan (that you do not have) OR a motorized damper for combustion air that you also do not have. The relay closes on a call for heat from the thermostat and opens the damper from its minimum position to allow combustion air into the firebox. As long as there is solid fuels (wood) in the heat chamber, the fresh supply of combustion air will allow the fire to burn or begin to burn very quickly.

As the temperature in the wood furnace plenum increases, the automatic fan control will start the fan and it will run as long as the bonnet temperature is higher than the fan'on' setpoint on the fan control... Now the house warms up and the thermostat satisfies which allows the combustion air damper to spring back to the minimum position, causing the hot fire to die down due to lack of combustion air.

The now smoldering fire will not generate enough heat to keep the fan running too long, so the automatic fan control shuts the fan off until the house cools approximately 2 degrees below thermostat setpoint. The thermostat calls for heat and opens the damper and on goes the cycle....

An important item to remember is that on the automatic fan control, there is a 'limit switch' function. The motorized combustion air damper or the combustion air fan must be wired through the limit switch in case the bonnet temperature exceeds 200 degrees F. This function will then allow the damper to go to the minimum position or the combustion air fan to go off, causing the fire to cool down due to lack of adequate combustion air.

You don't want the thermostat controlling the circulating fan directly, because of two things: 1). If the fire is out, there is no heat to circulate but the thermostat wouldn't know that and it would start and run the fan continuously until a fire is built. and ....
2). You would still be running up and down the stairs monitoring the fires burn rate by opening and closing the lower door manually.

ALL the components you need are readily available from WW Grainger....basically : a fan/limit control
a thermostat
a 110v x 24v 40 va control transformer
a 24v spdt relay
20 ga. two conductor thermostat wire
24v actuator and linkages to mount to the existing combustion air damper. A bit of creativity is required here. I would not recommend retro-fitting a combustion air fan.
14-2 wg romex for wiring the fan control

Again, it depends to what extent you are willing to go to achieve the end result. Will it be exactly like a new system?? No, but it will operate a lot better than that which you describe.
Oct 24, 2014 • Home
0helpful
1answer

My Ruud furnace used to regulate 1 deg +\- the set temp. Now it regulates right at the set temp and the fan cuts off while the burner continues to fire for a minute or so then the fan kicks back on for...

Hi,
It appears to be the fan limiter switch. It comes on at a certain temp when heating up and shuts off on the high end of its setting. Once the burners are shut down, the fan continues for a few minutes to cool down the burners. The limiter switch is adjustable but it sounds to me to be defective and should be replaced. Good luck and stay warm, :-)
0helpful
1answer

Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...

Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
0helpful
1answer
0helpful
1answer

My lennox furnace kicks on, then it shuts off

It should have a diagnostic set of leds on the board, with the code list on the door and the control board itself. If it get to the pilot stage and the shuts down its most likely the gas valve. You can check for continuity from mv to c on valve, you should have it. Then with a valtage test from mv to a ground or common as you here the next click of a relay on the board after the pilot has had a few seconds.
Not finding what you are looking for?

137 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...