My gas goodman heater will not ignite.
The blower starts and the ceramic piece lights up and then turns off after it fails to ignite. For the past few weeks it has had a hard time starting and staying lit. The light blinks once- the door says that this is a ignition failure?? What is wrong and what needs to be replaced???
Frank Bryant Wetzel
Level 3:
  • Master 456 Answers
  • Posted on Jan 15, 2010
Frank Bryant Wetzel
Master
Level 3:
Answers
456
Questions
0
Helped
121771
Points
1116
It is probably not the glow coil, if this is a 80% regular
furnace, Make sure the induced draft blower is working. I once went to a house where I came across
this problem, the only difference is that it would acutually start and then shut off. I took the vent apart
at the furnace and found a bird that was preety cooked.
If this is a90% High Eff. furnace, make sure the pvc
vents are not plugged. To troubleshoot the intake
Vent. Remove the combustion plate and then turn
the unit on, if it runs you have a problem with the
intake vent.
You could temp. remove the exhaust vent and then turn on the power if it runs then your exhaust vent
is probably plugged. You could go outside and make sure the vents are free.
Make sure you have gas available, these are the most commom issues that could solve your problem
I have a goodman gmp075-3 furnace, blower and igniter are working fine but not getting any gas to get furnace going
Check if 24 volts is being sent from the board to the gas valve, if not the board is nad and will need to be replaced, if there is 24 volts at the gas vlave terminals then the gas valve must be replaced.
By ocbjfrei on Mar 02, 2010 the heater starts, blower turns on, ignitor gets red, i hear a click for the gas and then nothing. why wont it light? I read the igniter could be bad even though it gets...
Hello, you should be getting 24-27 volts at the gas valve. If you have a multimeter you can read the resistance of the hot surface igniter it should be betwwen 40-90 ohms, if it is above this than replace the igniter.
1helpful
On my goodman gmv95 blower starts, glowplug lights, gas turns on, then glowplug goes out and gas shuts off. any suggestions what the problem could be?
You did not mention how long the main burner stayed on. If it stayed on only a few seconds, most likely you have a dirty or bad flame rod. The flame rod is located in the flame path of the last burner to ignite. Take a toothbrush and scrub off any debris that may be on it. Also check all the wire connections from the rod back to the circuit board.
1helpful
My Goodman heater has a problem igniting at times
Hi, I would have to assume your igniter is weak or has a crack in it. Do you see glow from the igniter every time? There is a flame sensor that looks for flame after the gas comes on and it will lockout after three tries, if the flame came on and shut back down every time, it would be problem with that.
4helpful
2answers
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
2helpful
3answers
My goodman gmt090-4 shuts off about 10 sec. after burners ignite
Check the pressure sensor. I tapped on mine a few times, removed the hose and checked it for blockage and replaced. It has been working fine since. I do have a new sensor on order.
No heat, trouble shooting light has continious flash.
There is a vacuum sensor on most units tied from the exhaust gas fan to the sensor. Does the unit try to start? If the unit's exhaust fails to pull the switch it will turn off after about 30-45 sec after starting. "IT" thinks it's not exhausting and stops to keep from overheating. Do you have this exhaust fan and rubber hose to sensor? Can you see if that fan is turning on start?