SOURCE: goodman gas furnace power vent motor and housing replacement
You need to type GOODMAN GAS APPLIANCES into you browser to find you local servicecenter. I must tell you that Goodman only sells to authorized service companies in my experience. So you become EgKraft Company.
SOURCE: New honeywell thermostat on new gas furnace not working
sometimes there's a differential setting anywhere from 1-3 degrees, see if you can make sure it's down to 1
SOURCE: furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
SOURCE: Furnace doesn't reach desired temperature
One of two things you can try. Do you own a volt ohm meter? Anytime your unit cycles short like it is doing the control circuit which on this one is 24 volts that engages relays and controls the gas valve to open and close. I am thinking the heat exchanger is getting so hot it is tripping the upper limit which for the most part is around 180 degrees. So next time it turns off take your ohm meter and with the power to the whole unit off. Either turn the breaker off or there is a light switch that is real close to unit turn it off. Undo the two wires to the gas valve and ohm them out. You should have continuity if you get nothing check each limit switch should have a couple. Undo wires to them and check. If you find one that is open more then likely the upper one. They are a safety device that keeps the unit from getting too hot.
There might be another option increase the speed of your fan motor to get the heat out of furnace quicker. Look at the circuit board notice the fan wiring going to it. The Red wire from fan is low speed look to see if it is on HEAT on the board. You should have 4 speeds to pick from you could take the black off of COOL and swap wires and test the unit by doing that. I'm going to put a solution on this so I can come back to it quicker. Even though we a just testing it for now. ken
SOURCE: Goodman GMNT furnace goes into 'lock-out'.
check to see if your intake pipe or vent is clear this could cause a flame jump and make it look like a bad flame sensor let me know if this helps