Control transformer keeps shorting out
One or more of the solenoids operated switches is your most probable cause. If you have a clamp on amp meter, measure the amps pulled by each component with a solenoid. The reversing valve solenoid and the main contactor solenoid. Each one of the these components are typically rated at 6watts. If your control voltage is around 25 volts, your amp draw should be about .24 amps max. If your transformer cannot be reset without blowing, install a 3 amp inline fuse so when the overload occurs the only thing that blow is an inexpensive fuse costing about 25 cents instead of a several dollar transformer. If your fuse/transformer immediately blows, try looking for a direct ground in the control wiring. If problems has persisted for a while, you may even have to look into replacing your thermostat wire. The control wire travels over the thermostat wire throught the thermostat and excess amps through the thermostat wire can break down the insulation jacket and short to the common wire causing the control transformer to blow. Another thing to check is the condition of your thermostat wire to check if the insulation is shredding off. Old thermostat wire, especially thermostat wire exposed to sunlight deteriorates quicker. Hope this helps.