Hi, here is the error codes that I could find for you, it seems you are overloading the inverter. That means you cannot connect a kettle or other heavy load to the output. See all error codes below, hoep this helps.
Problem: The AC load will not operate, error code shows on digital
display and alarm is sounding.
Error Possible Cause Solution
E01 Low voltage shutdown because battery is discharged.
Recharge battery. Shorten cables or use heavier cables.
E02 Over-voltage shutdown because of high input voltage.
Verify the charging system is properly regulated and the battery
is 12 V nominal.
E03 The AC product(s) connected are rated at more than the
inverter's continuous power rating; overload shutdown has
occurred. Use a product with a power rating within the inverter's continuous power rating (see Table 3).
E04 The inverter has overheated due to poor ventilation.
Overheating shutdown has occurred.Turn inverter off and allow to cool for 15 minutes. Clear blocked fan or remove objects covering unit. Move the inverter to a cooler place. Reduce load if continuous
operation is required.
E05 The AC products connected have a surge power that exceeds
the Digital Inverter's surge capability or the AC products connected are short-circuited and shutdown has occurred.The products exceed the inverter's surge capability. Use a product with a starting surge power within the Digital Inverter's capability.