Shawn whicker Posted on Apr 28, 2014

Carrier 30GX chiller keeps tripping on ground fault.

Why does my carrier chiller 30GX keep tripping on ground fault code 5.5

1 Answer

Robbie Daniels

Level 1:

An expert who has achieved level 1.

Hot-Shot:

An expert who has answered 20 questions.

Corporal:

An expert that has over 10 points.

Mayor:

An expert whose answer got voted for 2 times.

  • Contributor 25 Answers
  • Posted on May 19, 2014
Robbie Daniels
Contributor
Level 1:

An expert who has achieved level 1.

Hot-Shot:

An expert who has answered 20 questions.

Corporal:

An expert that has over 10 points.

Mayor:

An expert whose answer got voted for 2 times.

Joined: Jun 18, 2009
Answers
25
Questions
0
Helped
7884
Points
45

You need a megohmeter to test the line voltage wiring AND the compressor.

2 Related Answers

Anonymous

  • 1515 Answers
  • Posted on Mar 18, 2010

SOURCE: model 30gx faults code

Hi, the indoor chiller unit blower section will have a sheet glued to a panel on the unit that will tell you where and what the code 302 means on the unit. Then you will be able to make the repairs you kneed.
Shastalaker7
PS the numbers above show that this is a 3 ton unit, 38CKC036. The error code more than likely will be 3 flashes from the board followed by 02 flashes. I may be wrong on that , so correct me if I am.


Ad

Anonymous

  • 82 Answers
  • Posted on May 10, 2010

SOURCE: model 30gx faults code

The 30GX lists only 2 digit fault codes..here - http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/30g,h-3t.pdf

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
1answer

Siemens QF230A keeps tripping after installation.

So likely you have a 3 wire dryer cord and a 3 wire branch circuit. The dryer neutral is bonded to the dryer frame and the third wire of the dryer plug.

There were code exceptions for dryers and stoves that allowed timer motor circuits to use the neutral as a current carrier and frame ground.

To use the GFCI for the dryer you will be required to add an additional conductor (new 3 wire+ground cable) and separate the neutral to frame bond in the dryer and use a 4 wire dryer cord.

Likely you also have some GFCI single pole breakers and replaced ungrounded receptacles with grounded (another code exception) and they work OK. The dryer and stove are different as there is current on the third wire where as on the ungrounded receptacle GFCI there is no 3rd wire.

In breif, the neutral (current carrier conductor) from the dryer must be isolated from the dryer frame and dryer ground (fault current carrier conductor).

Or just leave it the way it was.

Check with local authority with jurisdiction for local code requirements.
0helpful
1answer

Carrier Chiller has fault code U65

What is the model number?

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

1helpful
1answer
0helpful
1answer

Error code 112. what is the problem?

Hi Pramesh

Not a normal carrier code, there may be a point between the 1.12 or 11.2

1. xx normally compressor 1 fault
2. 1.12 is compressor 1 condenser entering water thermistor fault, the unit will continue to run

http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/30g,h-3t.pdf

If you follow this link you should be able to download the manual for this unit and that may help you further

Regards

Gordon
0helpful
1answer

Carrier Screw chiller Model number PGI 225 -Y920 ,Ineed Trouble Shooting

You really need to talk to the carrier people for a solution here.
There are too many variables to be sorted out to give you a solution on line
0helpful
1answer

I have a Carrier HFC-134a commercial chiller unit model 30HXA076RY-561AA. It runs 2 sides which are labeled A1 and A2. Over the past few weeks now the A1 side keeps shutting down (almost daily sometimes...

To start with, the more I look at a system, the more familiar I become with that unit. Also, these machines can make me look like a genius or a fool! If you have a pressure switch problem, it's more than likely an expansion valve issue. I've seen a 2 month old Carrier, 4 compressors at 6 tons each, fail due to their expansion valve having an intermittent miss, closing for no reason, or not opening upon demand. And I spent 3 weeks chasing this because when it fails, all you can do is see the code, troubleshoot a bit, call Carrier tech support, then reset it. I ended up calling out Carrier, yes they have field techs, and it took 2 of them about 5 hrs to figure it out. These 2 only work on chillers, and took them 5 hrs! They adjusted the settings and walked away from it, said it was cycling on to close(each circuit), had damaged the valve. Still under warranty but did not replace. If its not the cooling fan circuit acting up, it may be the expansion valve(s) acting up. In that scenario, the tech is going to need to camp out by the unit, and catch it in the act. If you get a second opinion, call a refridgeration company that has some background in chillers. Or call Carrier.Hope this helps!
0helpful
1answer

Model 30gx faults code

Hi, the indoor chiller unit blower section will have a sheet glued to a panel on the unit that will tell you where and what the code 302 means on the unit. Then you will be able to make the repairs you kneed.
Shastalaker7
PS the numbers above show that this is a 3 ton unit, 38CKC036. The error code more than likely will be 3 flashes from the board followed by 02 flashes. I may be wrong on that , so correct me if I am.


0helpful
1answer

Air conditionin gunit keeps tripping breaker. A/C is carrier 5 years old compressor?

Sounds like you have a grounded compresser with a direct short.To know for sure you can disconnect the compresser and then flip the breaker and see if it still trips.If it still does check the motor,but this is most likley the compresser sorry.Carrier does have a 5 yr warranty so hurry and call someone it could still be in warranty!
0helpful
1answer

Carrier 19DX liquid chiller trips in 68

are the coils dirty? How about the filters? Is there ice build up on coils towards the bottom?
Not finding what you are looking for?

333 views

Ask a Question

Usually answered in minutes!

Top Carrier Heating & Cooling Experts

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Grand Canyon Tech
Grand Canyon Tech

Level 3 Expert

3867 Answers

Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...