I have a intertherm T3RC-036K and the label is faded away. Would like to know the design pressures for the high and low side.
or someone point me to a site where i can find the info. thanks
I don't use design pressures due to many variables such as ductwork, humidity, blower speed, o.d. temp, I.d. temp ect.... Learn SUPER HEAT AND SUBCOOLING values. Most guages give a pressure/ temperature relationship. At a pressure there is a temp that lines up with that pressure. If its r22 the temp is in the green and pressure is in the white(normally). If r410a temps in the pink. R22- Most evaporator are good between 40-50°F. If your coil is operating at 45°f your superheat value should be 10°-18°. Take the actual temp of the suction line(large copper line that's cold) and subtract that # from the temp on your gauge. The value should be 10-15°. Same on the liquid line. You o.d. coil is usually 90-105°F. The liquid line temp(small copper tube that's warm) subtracted from the pressures temp gives you the SUBCOOL value.
R410a? Subccoling
R22? Superheat and subcooling
If it has an expansion valve? Sub cooling
This method is used to take all the guesswork out of the scenario. BUT! Most of the machines will have a data plate that gives great info for this method. But some only give it in the owners/installation manual. You won't get a good answer to your question but this is the correct way all HVAC technicians SHOULD check freon levels and is the only way if we are achieving designed efficiency. If you know its low on freon, again most coils are "happy" between 40-50°F(68-84psig). And at that temp your high side should be 90-105°F(168-210psig). And again, so many variables! I usually shoot for 95°f o.d. temp, 80low 210high psig and 10° SH 12-18°SC.