Goodman GMS90703BXA Heater Logo
A
Anonymous Posted on Feb 12, 2018
Goodman GS9 blowing air but not getting hot
The Goodman GMS9 is blowing air but it never gets hot. We unplugged it several times and then needed a new fuse. The LED was lit continuously so we finally replaced the thermostat. The furnace fan is still blowing air but again it is not hot. What are some possible or common causes of this?
Andy
Level 3:
Loyalty:
Visited the website for 30 consecutive days.
  • Master 572 Answers
  • Posted on Feb 12, 2018
Andy
Master
Level 3:
Loyalty:
Answers
572
Questions
0
Helped
209463
Points
1498
Does furnace fire up ,if not you have a issue with your furnace and not thermostat
5 Related Answers
Anonymous
  • 69 Answers
  • Posted on Dec 21, 2008
SOURCE: Furnace start buts shuts off
It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve
Anonymous
  • Posted on Dec 30, 2008
SOURCE: 1993 goodman status light 4 times blinking
I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??
David Shaub
  • 2994 Answers
  • Posted on Nov 20, 2009
SOURCE: Need to find the pressure switch on my goodman furnace
It's mounted onto the gas valve. It will be a button or lever that you have to push in or down, depending on the style.
Anonymous
  • 767 Answers
  • Posted on Jan 02, 2010
SOURCE: My furnace heats the house well, but during the
Depending on the age of the furnace you may be able to adjust the cool down. On some furnaces there is a silver box usually made by honeywell. This is your fan limit control. If you take the cover off you will see a dial with different temperature settings with 3 pins in a grove. The first one is fan on with temperature rise this turns the blower on when the furnace starts and warms up. The second is the fan off after furnace shuts down, this would be the one you want to adjust to a higher temperature to keep the blower from blowing cold air. The last pin is the high limit if the furnace gets to this temperature it will shut the furnace off but keep the blower running. Make sure that the thermostat fan option is set to auto and not on.
Anonymous
  • 111 Answers
  • Posted on Jan 31, 2010
SOURCE: Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Cond fan motor runs for about 10 sec then cut off
sounds like it is getting hot need get a can of conpressed air and blow it out.
1helpful
Goodman model aruf486016AA is not blowing hot air
Need more info. Does blower come on when calling for heat?
New goodman 2.5ton and 2.5-3.5 airhandler installed 8weeks ago, worked well for about a week, then the problems begain, heatpumps reversing value replaced already, but unit still does not cool well,when...
There could be several things wrong. The unit could be undersized but since it worked fine in the beginning, we'll rule that out. There could be a refrigerant leak. Check and see if the evaporator coils (inside furnace) are sweating all the way to the top. The new refrigerant in these units makes it absolutely critical they be charged correctly. The expansion valve also requires adjusting sometimes, if so equipped. Just keep talking to the installers. It sounds like they will eventually get it right for you. Sometimes it takes several trips to get everything adjusted perfectly.
Fuse blow each time I turn on air check for
disconnect the thernostat wires from the control board. Put a jumper wire between R & G put door back on and turn on power. Blower motor
should run, if it blows the fuse then you have a direct short between R &
G at the board. Do this with R and W(heat) and R & Y(cool).
By disconnecting the thermostat wires and reinserting them make sure that they do not touch when inserted into each terminal. If it still blows
that little 3amp fuse when jumpering between each sequence as mentioned above, then I think your board is bad. When Jumpering out the Y terminal you will have to have the AC wires still hooked up. If it
blows the fuse in that sequence. Disconnect the wires out at the condensor.
You mat have a bad contactor at the outdoor unit.
New heatpump suction line gets hot when ac is calling hooked to new 95% goodman furnace
Is it blowing out hot air? If so, unit could be wired backwards or you are having problems with reversing valve
I have goodman CKL49-1, air is not blowing, the
Your evaporator fan motor has quit. You need to find out if it is a relay or the fan motor. These systems come in various different setups. Updraft (vertical) or lay down (horizontal) you have to gain access to the motor and get it out. Turn off all power to the unit, look for any breakers at the panel. open the panel usually the same panel to access the filters. The motor and squirrel cage fan, will come out as one. look closely for rails at the top to slide the motor and cage out. Your wiring should unplug from the top close to the capacitor. you then can unbolt the motor - take pictures so you can reassemble it. Take the motor to a local HVAC store for a match. Be sure you get a new capacitor to go with the new motor.
3helpful
My furnace heats the house well, but during the cool down it actually blows cold air dropping the temperature causing the furnace to re-ignite. How do I adjust? Goodman - GMS9/GCS9
2answers
GOODMAN GMS9 limit switch
check the temp on the switch.Any switch will work as long as it has the same temp setting.
Top Goodman Heating & Cooling Experts
Paul Carew
Mike Cairns
Mike Cairns
Jay Finke
Jay Finke
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others