Tim J Posted on Nov 27, 2012

Generac model 60511 10kw, 240VAC is ok, but 210VAC-gnd and 80VAC-gnd?

I just got the generator installed and when performing voltage checks I discovered there are 240VAC on the phase OK, but when I checked each leg to neutral/ground, I found fluctuating voltages. On one leg, the average was 208VAC, on the other the average was 84VAC. All of these voltages were read under no load conditions. I am reluctant to load the generator until I can verify these are not dangerous conditions. Thanx for any help.

5 Related Answers

Anonymous

  • 169 Answers
  • Posted on Jan 26, 2009

SOURCE: Generac Guardian 15kW Generator

That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.

You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.

Regards,
Carl

Ad
mamicheddy

mamicheddy

  • 79 Answers
  • Posted on May 07, 2009

SOURCE: generac model # 09734-1 no voltage output. would like a manual

Flash the fields. Remove front cover from the generator end. You will see the brushes and rings on the rotor. The ring closest to you is positive and the ring closest to the rotor windings is negative. With a 12 volt batttery and the generator running, place the positive side of the battery to the ring towards you and negative to the back ring. Make sure to use jumpers and keep fingers away from rotating parts and don't get zapped. You should see output voltage increase. If it does, your voltage regulator is bad, if it doesn't your generator end is bad.

Anonymous

  • 384 Answers
  • Posted on Sep 08, 2009

SOURCE: 10kw Generac Guardian not cranking, shows rpm sense loss

Sounds like Generator mode switch should be "ON".

Sheldon Dedek

  • 912 Answers
  • Posted on Jan 04, 2010

SOURCE: Generator was running and quit delivering voltage

It very well may have been a breaker that opened up permanently.

But, I bet that the generator was under heavy load for prolonged time, and one / both of the diodes in voltage regulator have opened up. You will have to disassemble the end housing of the alternator to get to these, and then test with multimeter to know for sure.

Of course, your generator may have an electronic controller, and not use diodes / capacitor at all. Since don't have model #, can't be sure.

If engine has dropped much under 1800 (4 pole alternator) or 3600 (2 pole alternator) RPMs, then alternator output would tank or be nonexistent.

Anonymous

  • 710 Answers
  • Posted on May 07, 2011

SOURCE: Just returned from a trip

Hi Scott,

Since the generator starts but there is no power to the control board, there is an electrical problem inside the generator.
First check the circuit breaker at the back of your generator. If the breaker is on, then your generator is in serious trouble.
Call a repairman, but also keep in mind you may need a new generator.

Hope this helps. If it does, I'd appreciate a 4 thumbs up. Thanks,

Handie Andie

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

13w guardian generac generator 054960 doesn't charge battery

Check "F1" fuse.

If fuse is good, check voltage at battery.

With either utility power present or generating running, the voltage at the battery should be >13VDC. Any reading less than 12.7VDC is battery voltage and indicates a failed charging circuit.
0helpful
1answer

Which would be generic voltage regulator compatible with the generator?

I need to know the open circuit voltage of the generator, whether DC or AC and then what voltage and current you wish to obtain and regulate to. Thanks
0helpful
1answer

I have a generac mc alternator model -38 6938 my voltage pulsates underamload just started any ideas

Cleaned and adjust carburetor per Repair Manual. then adjust governor repair manual and should take care of problem on this old generator.

https://www.generator-parts.com/manuals/generac-rv/051834.pdf
0helpful
2answers

Generac troubleshooting

Check that there is not a switch to activate the panel. Next, there is a fuse for the outlet panel as well or a circuit breaker. Check that. If all of that is good you will have to put a meter on all of the wiring points from beginning to end and find out where the voltage stops. Then you have found the component that went bad.
0helpful
1answer

My generac generator is producing low voltage

check voltage input at voltage regulator, then check output from
the regulator.
0helpful
1answer

Generac 40kw single phase generator starter engages after 30sec of running

For the over voltage there is an adjustment on the control board.
Should be tested with a load something plugged in.
The hertz might just come on when under load and adjusted too.
If you need more give a model number and whether it is 13kw or 40kw.
2helpful
1answer

New Generac Generator--Battery Goes Dead

Yes,if its working correctly,you should be getting a reading about 2.5 to 3 volts above the battery voltage rating while its in standby mode.
2helpful
1answer

How can the battery charger be changed?

Yes this is a very simple job to do. there are only 2 small bolts holding it in. Make sure the generator is in the off position and removed the 2- 5amp fuses in the transfer switch for N1 and N2 Use a fuse puller designed for this (you can get at home depot or lowes for around $9-$10) not a pair of pliers or screwdriver, etc... there is 240VAC on these fuses.. N1 and N2 are what ultimately feed the transformer in the generator which steps the voltage down to 24-26 VAC and feeds the battery charger. Other than that its fairly simple, let me know if you have any more questions.
1helpful
1answer

Guardian generac 10kw model 5502 does not output correct voltage

the instructions says the voltage regulator is automatic/digital. when you check the voltage is there any load on the generator? if applying load to the generator doesn't help, you can manually change the motor speed where the governor connects to the carborator, but it may change the frequency, but the regulator may fix it
Not finding what you are looking for?

140 views

Ask a Question

Usually answered in minutes!

Top Generac Electrical Supplies Experts

vince

Level 3 Expert

2530 Answers

Brad Brown

Level 3 Expert

19187 Answers

Paul Bade

Level 3 Expert

1818 Answers

Are you a Generac Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...