I tried to turn heat on but heat strips don't come on so i checked voltage got's power going to the sequerncer so i went to the stat and turned the stat off but it would not shut off i unplugged the wires to the stat and the air handler keeped running would not turn off
Keep in mind that you need high and low voltage at your sequencer to bring your heat on. Or any relay for that matter, unless a high voltage coil, the 24 volts energizes or closes the circuit therefore bringing on the load.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Maybe a bad sequencer.unplugged wire from sequencer and see it unit shut off .Sequencer is typically a relay
SOURCE: installing new furnace with two zones
You will need a control to operate motorized zone dampers. In the ductwork, you will install a damper in each line going into the area you want zoned. If you have air conditioning you will also require a barometric relief damper that allows air to pass thru the ductwork and not restrict air over your A/C coil. Common controls are made by Honeywell and EWC.
If you already have the control module, you will run two or three (low voltage) wires from each motorized damper back to the control. Your thermostat wires (also low voltage) will run from each thermostat to the control module and connect to a zone relay. Match each zone by number. You will need to run power to the control module that will provide power to the thermostats as well as the motorized damper. Check on the reverse side of the control module and/or check on the web to find the wiring diagram.
SOURCE: ELECTRIC HEAT STAYING ON IN COOL MODE
Disconnect the white wire from the "thermostat". If the strips stay on its your thermostat wires.
SOURCE: GMPN 100-4 furnace. Blower motor runs when not calling for heat.
The board is bad. The unit thinks a flame is present, so it tells the blower to come on. Replace the board.
SOURCE: goodman 075-3 fan runs but no voltage going to igniter
One thing you can checkmis the continuity through the ignitor itself if you have continutity through that there is also some safeties it has to go through but the board is where the voltage is supplied for the ignitor. I would check the high limit and the roll out before condeming the board.
SOURCE: I have a Goodman AR36-1 air handler. when I turn
Hello Your motor is shutting of thermal overload because of an internal problem.New motor time,Pull it and match it up the info is on the side of the motor.