SOURCE: i have a goodman gmp075-3 and it is flashing # 4 code
There is a Primary High Limit Switch towards the middle of the furnace, it more than likely needs to be replaced, very common to go out only after a few seasons. Also, you could have a flame rollout switch tripped that will signal the same code, these switches are re-settable and are located on the outer, top and sides of the burner assembly, they’re about ½ inch in diameter with a red push button in the center and two wires “ usually purple” coming off of them.
Hope this helps
SOURCE: 1993 goodman status light 4 times blinking
I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??
SOURCE: Goodman furnace GMPN080-4 Getting 4 RED blinks/Open Limit Swtch
You have a limit switch located in the furnace (a little bigger than a dime and located near the center of the front panel, sometimes the switch is mounted to a small fiberglass board) . There will be two wires going to it. They sometimes trip so often that they fail to automatically reset(due to dirty filters or undersized ductwork). You can SHUT OFF POWER TO THE FURNACE, then remove the two screws holding the switch in the furnace, pull the switch out of the furnace and tap on it and wipe it off.
The switch may work a few more times but should be replaced with the same size and type. You will see some rating printed on the switch somewhere. Write down all the numbers and get a replacemet from a furnace/AC supply house. If you have a meter and know how to use it you could check the switch for continuity.
Sometimes just a tap on the switch will get it going. There will also be a couple of rollout switches that could be tripped. They have little buttons on them to reset them. If they trip it may have other issues to be solved.
Hope this helps!
Matt
SOURCE: goodman furnace 4 blinks
Ohm out the safety switches also known as the high limits usually at least two on units they look like little buttons, with two wires going to each one. An open high limit will mean the circuit is not closed and allowing for the system to complete the circuitry to fire the heat, best way to diagnose is to jump out the suspected high limit s/w if the unit runs then you have your answer, but never, never leave the high limit switch jumped w/o the switch.
SOURCE: I have a goodman GMP 125-5 furnace. I have
sounds like the primary limit typically behind the gas valve its larger then the others, rectangle in shape with 2 wires going to it. be careful if your bypassing limit this can create a very hazardous condition