Goodman CKL42AR42 Air Conditioner Logo
I have a gmp-1254 gas furnace. The fan runs and the controller card blinks 4 times but gas does not come on. Any suggestions?
5 Related Answers
Anonymous
  • 182 Answers
  • Posted on Nov 03, 2008
SOURCE: My Goodman gas furnace will
hot surface ignitor is my guess
Anonymous
  • 1420 Answers
  • Posted on Dec 10, 2008
SOURCE: Goodman Furnace GMP 050-03
You need to check for 24 volts across the gas valve as the ignitor glows. If you get it, it is a bad gas valve. If there is no voltage or strange voltage, replace the control board.
Anonymous
  • Posted on Dec 30, 2008
SOURCE: 1993 goodman status light 4 times blinking
I have a goodman GMP075-3 that won't turn on. I think it is the pressure switch since I do not have a vent blockage. What is a venter and where can I find it??
Anonymous
  • 3600 Answers
  • Posted on Oct 09, 2009
SOURCE: How to fix twinning problem for a goodman GMP 100-4
Call AAA back it should be warrented if they worked on it frst don't touch it or you lose your warrent, it does sound like the thermal bulb is not in the flame so call them back fist then let me know post here and I will try to help you if they do not sove the problem, you should have a work order they gave you when they did the repair. Hold on to it.
Testimonial: "The thermal bulb would cause the twinning light to come on."
Anonymous
  • 614 Answers
  • Posted on Nov 04, 2009
SOURCE: goodman gmp 125-4 gas trouble code
Rewire to schematic specs and check po;larity of transformer. Rus
1helpful
I have a goodman gmp 100-3 furnace..It will run for about 2 minutes when the flames kick on then it shuts down burners and the inducer and the blower motor still runs with no flames..It throws a 4 bli
It would be nice to know if this is a condensing furnace or not. With the lack of information, I cannot suggest that there could be a problem originating from a plugged condensate drain or a blocked combustion air inlet pipe on a two pipe furnace or a blocked flu pipe.
If it has only one pvc pipe, that will be the flue and it could be partially blocked with mud daubers or another critter. A blockage in either will effect the flu's positive pressure and possibly open the pancake style pressure switch causing no gas but the indoor blower will still run because it is energized off of a circuit board and not a thermal sensing switch.
Of course, you could have 80% furnace with galvanized flu connection to a masonry (or metalbestos) chimney and it won't have all the sophistication in the control circuit that the 90 percenters have. 80 percenters also have an inducer motor, but they don't have the condensing coils of the more efficient.
This probably wasn't a lot of help, but maybe the door still has the troubleshooting chart on it that tells you what the blinks mean. That should put you more in the right direction than a stab in the dark. Seldom is too much information provided within a question.
Have a gmp 125-5 furnace and light blinks 5 times
Here what i found , five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
2answers
Janitrol gmp gas furnace ignitor troubleshooting 125 blink
if it is shutting off abruptly the limit is either wired wrong or set wrong. If the fan comes on and blows the flame out there is a hole in your heat exchanger which can result in fire or carbon monoxide poisoning. Have an experienced tech take a look at it to be safe.
Module doesnt blink
Generally a control module won't diagnose that it is bad. The fan switching in heat mode occurs via timer in the board. So either run the fan on all the time from the thermostat, or replace the control module.
BGU10016A BLINKS CODE 9
www.repairclinic.com/Shop-For-Parts/a36b383/Coleman-Furnace-Parts
Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...
Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
8helpful
2answers
Goodman GMP 125-4 one blinking light code. Gas valve has been replaced (at cost of $443). Didn't fix problem. Same co wanted $415 to replace circuit board. I did it myself for $99 part. Still same problem!...
One blink means it didn't light after a number of attempts. You replaced the circuit board and gas valve. Read on for some suggestions. On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
2answers
I have a goodman GMP 125-5 furnace. I have
sounds like the primary limit typically behind the gas valve its larger then the others, rectangle in shape with 2 wires going to it. be careful if your bypassing limit this can create a very hazardous condition
Goodman furnace\ blower comes on,unasked
Sounds like the fan switch on the furnace is set to low. Turn power off to furnace, take door off of furnace look for a fan switch, it may be a fan - limit together. The limit settings should be approximately 160° to 200°, and the fan settings should be about 100° to 140° set it to 120° it it's already set there then you probably need to replace it.