Startup/Shutdown Procedure for SILCON 10— 8OKVA
Startup:
1. Switch on the mains power supply Display shows - System type and kva
2. Wait about 10 seconds Display shows - Stop charge DC caps yes
3. Press C on the keyboard Display shows - Start charge DC caps yes
4. Press # on the keyboard Display shows - Data Stored
5. Wait about 1 second Display shows - Start charge DC caps yes
6. Wait about 1 minute Display shows - Insert DC fuse or close MCB
7. a) Systems with internal batteries DP310/340 Display shows - System Off
insert fuses F020 and F021
b)Systems with external batteries. Close battery MCB's You have a 30 second window to attach the battery.
8.Press the "Green On" pushbutton Display shows - Normal Operation load xx%
Shutdown:
1. Press # to enter parameter stack
2. Press up or down until Display shows - Bypass Operation : No
3. Press C until Display shows - Bypass Operation : Yes
4. Press # to store
5. Press drop down arrow (enter key) to exit Display shows - Bypass Operation load %
6. You can now open the battery breakers
For more procedure go HERE
Electronics - Others Logo
i have to unplug wait for the power light to stop flashing red multiple times before it will come on
When the TV does this, the RED LED on the front will blink. For digits 1-10 it will blink pause then repeat. For numbers with 2 digits it will blink the first digit slow and then second digit fast. So 25 would be 2 slow blinks followed by 5 fast blinks.
Error Description Error/Prot Detected by Device Defective module Result
1 I2C1
2 I2C2
3 I2C3
4 I2C4
5 VIPER
6 5V supply
7 8V6 supply
8 1.2V DC/DC
11 3.3V DC/DC
12 12V supply
14 Supply Class D amplifiers
14 Supply Audio part SSB
17 MPIF1 audio supply
18 MPIF1 ref freq
25 Supply fault
27 Phoenix
28 MOP
29 AVIP1
31 AVIP2
32 MPIF1
34 Tuner1
37 Channel decoder
39 POD Interface
43 Hi Rate Front End
44 Main NVM
45 Columbus
53 VIPER
63 PDP Display
2answers
Dc bus faulty
Batteries in the UPS typically last 3 to 5 years and it depends upon several factors. including the number of times the unit must go on battery power and environmental conditions. There are usually several batteries in the UPS and while the battery voltage may show 13 volts, this may only be a float charge/voltage and a true indication of the battery voltage and condition requires the batteries to be tested under a load. There maybe one battery in a set of batteries that is faulty and causes the whole battery system to fail and indicate a battery fault.
These lower powered and cheaper KVA type UPS are switch over types, when the mains supply fail, the UPS switches over to the inverter in milli-seconds which then supplies mains power but the power waveform is a pseudo sine wave (ie not a true sinewave. A faulty inverter circuit won’t deliver power when the mains supply fails.
The true UPS types are usually the higher KVA units (over 1500 VA) that supplies uninterrupted mains power. The mains power is connected to a charger which charges the batteries and the inverter draws power from these batteries and converts it to true sine wave mains power therefore there is no switch over time lag from the mains to the battery.
sir after changing the battery ups worked well one day and the next day onwards when i pressed the switch red and amber lights blinking and the upc trips with beep sound .kindly give the solution
2answers
e-5 error code
E5 code refer to fuser unit.To dfisplay both digits press the Enter.
E 52 Fusing error 1 Defective thermistor,heater lamp open,defective main or ac/dc drive board.
E 53 Fusing error 2 thermistor in shortcircuit,fusing harness shorted or ac/dc power supply board defective.
E 54 fusing error 3 main board or ac/dc board defective.
E 55 Fusing error 4 rhermistor open,defective main board or fusing lamp open.
When E5 service call condition occur for safety reasons they cannot be cleared by turn OFF/ON the power switch.After repairing the copier turn ON the main switch.Enter in the SP mode and press 97.Turn the main switch OFF wait 10 sec and turn ON.
3answers
my ups is switching off itself immediately the mains goes off.the battery is okay with 13v.
Batteries in the UPS typically last 3 to 5 years and it depends upon several factors. including the number of times the unit must go on battery power and enviromental conditions. There are usually several batteries in the UPS and while the battery voltage may show 13 volts, this may only a float voltage and a true indication of the battery voltage needs the batteries to be tested under a load. there maybe one battery that is faulty and causing the whole battery system to fail.
These lower powered and cheaper KVA type UPS are switch over types (when the mains fail, the UPS switches over to the inverter in milli-seconds to supply mains power). It is a possibility the inverter circuit is faulty and when the mains power fails the inverter does not switch over.
The true UPS type are usually the higher KVA units (over 1500 KVA units) that converts mains power continuously via the inverter circuit. The mains power charges the batteries and the inverter drawing power from continuously from the batteries (therefore there is no switch over time lag from the mains to the battery.
Top Electronics - Others Experts