Amana PTH123B25AJ Heat Pump Air Conditioner - Answered Questions & Fixed issues
2 problems.. AC Comp cuts out. And Fan will not stop.
Unit#2 -Sounds like the contacts on the master switch are welded closed or the switch is broken, Replacing the switch should fix this unit.
#1 is a little more difficult to diagnose. The compressor is being taken off line by a circuit that protects the compressor from damage either; 1- liquid refrigerant getting back to the compressor which can be caused by something as simple as a clogged return air filter or evaporator coil on a heat pump or 2- overload situation caused by a bad condenser motor or a clogged condenser coil. The first thing you need to do is clean both coils and replace the filter,. Then check to be sure your getting good airflow across both coils. I think it's most likely an airflow issue I hope this resolves the problem GL!
7/9/2021 5:33:18 PM •
Amana...
•
Answered
on Jul 09, 2021
•
952 views
Formula to calculate rating of capacitors in
It's not fixed formula, but as per basic rule, easy method tocalculate for motor capacitor.
(2650 X full load amps) divided by supply voltage(mentionedin capacitor)= MFD. (Plus or minus 10% to 15%)
Ex: 1 Tr which gives full load amps of 6 amps (2650 X 6)=15900 divided by 240(VAC)volts=66.25MFD
(10% to 15% plus or minus) You can fix 56.32 mfd or 76.18mfd
So, you can go in between 56.32 mfd and 76.18 mfd.
If you calculate of 440VAC capacitor, it will be 36 mfd.
Hope, it will be helpful . Thanks.
11/22/2019 11:07:01 AM •
Amana...
•
Answered
on Nov 22, 2019
•
831 views
I have an Amana ptac hotel type thru the wall
Hi,
If you reset the GFCI button and then when you go to turn it on the button pops again, then you have a short inside the units probably in the fan motor or the compressor..
heatman101
8/30/2015 2:56:57 AM •
Amana...
•
Answered
on Aug 30, 2015
•
2,049 views
My heat pump is shot and is operating off the
You mean you are using the Emergency heat setting instead of the heat pump????...You're using Natural gas only now tn emergency heat????That's fine...I wouldn't replace a heat pump if you have Natural gas....it's too expensive compared to Gas....you may be able to still use the heat pump as an Air Conditioner only , it depends on what's wrong with it...otherwise you will have to get a Central Air unit instead...cheaper and just use the Gas for heat
5/28/2015 2:47:11 PM •
Amana...
•
Answered
on May 28, 2015
•
463 views
Fan runs all the time and no heat
br means brown out protection engaged. Power was lost or voltage is to low, check for incoming power at correct voltage
3/12/2015 8:37:38 AM •
Amana...
•
Answered
on Mar 12, 2015
•
98 views
Heater, ac and fan speeds all working fine. Compressor not kicking in...just auxiliary heat working.
Outside temp too low, so outside thermostat and it's settings will not allow the heat pump to work. But insist on the ausilary heat to work instead. Heat pumps usually do not produce enough heat when below 40F outside temp. If you have Gas heat, it may be more economical than the heat pump below 40F. If electric auxilarry heat, it may compete at 32F. Talk to your dealer, installer, or manufacture.
3/4/2015 1:55:43 AM •
Amana...
•
Answered
on Mar 04, 2015
•
218 views
Why does the air conditioner works fine but no heat
A bit more info would help - like "nothing as in switched off" or "nothing as in motors all running but nothing gets hot".
If you mean that it all sounds and looks as though it is working but there is no heat, then it is possible your changeover valve is jammed. There is usually a four way valve which effectively decides which way your a/c is going to be pumping.
Other reasons are that on this model, it checks to make sure there is at least a 5C difference before it will try and work.
For more help, please be a bit more descriptive as to what it IS doing as well as what it is not - eg: fans / compressor on? strange noises, hissing / error messages and also indoor / outdoor temps
1/4/2015 11:11:38 PM •
Amana...
•
Answered
on Jan 04, 2015
•
101 views