Generac 6051 Guardian Series Air-Cooled 10kW 120/240V Single Phase Steel Residential Generator with Nexus Smart Switch - Page 9 Questions & Answers
How to check a starting capacitor on a generac generator
Disconnect wires and use a Fluke meter 16, typically used by HVAC techs. (It has a capacitor charge function) You cannot use a multimeter accurately. An old analog meter on ohms, will show a reading then decay, all that tells you is it isn't open, it does not tell you if it is holding correct mfd capacitance
3/1/2015 9:23:22 PM •
Generac...
•
Answered
on Mar 01, 2015
How to set up governor for Generac GN-220 motor
The circuit board controller is monitoring the engine rpm and frequency and thus controls the frequency, via the governor actuator, or stepper motor as you say. You can't adjust it. I doubt this is the problem it sounds like either engine is not delivering HP, or there is a stator short causing excessive load / current draw bogging the unit down, incorrect wiring of the stator output. Ha someone taken the stator output leads off the breaker? check the stator resistance and shorts to ground.
2/28/2015 10:53:11 PM •
Generac...
•
Answered
on Feb 28, 2015
What size wire to hook up a 15kw generator to my house
At 240v, a 15KW generator will produce appx 62A or 31A per 120V leg. Therefore allowing for some overload, a conductor sized for 35A per leg would be adequate, but you should verify local code requirements.
9/3/2014 7:43:47 PM •
Generac...
•
Answered
on Sep 03, 2014