1answer

Goodman cple30-1c air conditioner not running,

whats it doing?? humming?.............
8/10/2010 2:46:42 AM • Goodman... • Answered on Aug 10, 2010
0helpful
1answer

My dog chewed the thermostat

Either you have blown the low voltage fuse located inside the air handler (if there is one) or you have blown the transformer feeding the low voltage control wiring.

If the transformer is blown due to no fuse installed, I would recommend installing a low voltage 3A fuse in line with the red terminal coming off the transformer. This will protect the transformer in the future.
8/1/2010 4:24:02 AM • Goodman... • Answered on Aug 01, 2010
0helpful
1answer

Condenser fan will not turn on, although I can

Is the compressor running? If not then check the disconnect or fuses. If it is then make sure the fan turns freely and check the fan capacitor. Replace it if it is bad. If the capacitor is good then check the fan motor windings and replace the fan motor if the winding are open. Let me know what you find.
7/28/2010 3:58:57 AM • Goodman... • Answered on Jul 28, 2010
0helpful
1answer

My compressor tries to start but stop after 1

If there is a capacitor on the motor to kick start the motor in the correct direction, this could be at fault as the motor will just stall. Or the compresser could be seized up.
7/25/2010 7:15:31 PM • Goodman... • Answered on Jul 25, 2010
0helpful
1answer

The coil outside is 45 degrees but the air blowing

Is this a heat pump? If so it sounds like a stuck reversing valve.
Sometimes cycling the thermostat between heat and cool will free it.
7/24/2010 4:37:42 AM • Goodman... • Answered on Jul 24, 2010
0helpful
1answer

The fan coil in the attic is leaking water. The

The pan may of cracked, also check to make sure the coil is clean water may be running off due to it bening dirty.
7/18/2010 2:32:55 AM • Goodman... • Answered on Jul 18, 2010
0helpful
2answers

Where is the fuse box?

Does the indoor unit run?

It sounds like you're looking in the right place. Check your power panel for a tripped circuit breaker (maybe more than one) or if the home is older, it may have fuses. It's possible that the outdoor disconnect also has fuses but that's not as likely. You can check around the outdoor unit and see if you smell anything burnt.

You can aso turn off the unit at the thermostat, wait a few minutes and see if the unit starts back up, but check the items listed above first.
7/17/2010 11:38:06 PM • Goodman... • Answered on Jul 17, 2010
0helpful
1answer

Goodman cpl-j42-1a outside unit fan will not run i

The fan motor on the condenser not working can be a easy fix or the motor itself could be bad. One important thing is, if your condenser fan isn't coming on, but the compressor inside is running, you could cause a lot more damage and may have to replace the compressor also, which could get expensive! I will try to go through a few things to see if any fit your problem.
(WARNING) Before working on any part of the electrical system, or even opening the compartment, please disconnect all power to the unit!
1. Fan motor not running, but compressor IS coming on-

Bad Capacitor- Its a small round or oval part that is inside the electrical compartment on the outside condensing unit. You will have to have a multimeter that reads MFDs to check it. If you do have a meter, take off the connections that or on the Herm terminal, (if you have a capacitor with just two terminals, make sure you disconnect one side), set your meter to Mfds and touch your leads to both terminals. Remember the reading it gives you and compare it to the Mfd rating on the side of the capacitor. It should read something like 15mfds/5% 370v, they vary in sizes, but make sure that your capacitor is running close to what it's rated at, if not, then it needs to be replaced. This is a common reason the fan motor stops working when everything else is still working.

Bad Motor- This can be a little more complicated sometimes since a motor can go bad and not show normal indications. The first way you want to check is to try and turn the blades on the fan motor. It should turn freely with no problem, if it doesn't, it needs to be replaced. You can also check for continuity in the motor with a multimeter, but as I said before, sometimes it can show that its okay, but still have a problem. Sometimes when your fan motor burns up, it makes a loud humming sound when it tries to kick on.

2. Fan motor not coming on, compressor also NOT coming on-

Fuses on disconnect switch- There will be two fuses on most disconnect switches that are inside the disconnect on the outside of the house, usually right by the unit. (Some condensers do not have a disconnect at all, see BREAKER BOX) To check the fuses, you will need a multimeter that has a ohm setting, they should have continuity through them. Some fuses have a small window that you can see if they are blown or not. If so, replace fuses with the same size that was pulled out.

Breaker Box- Simply enough, sometimes your condenser will trip the breaker in the breaker box. Make sure all your breakers are switch to the on position. Sometimes this is all it takes and other times it can mean that there is a more serious problem. (If you reset the breaker and it automatically trips again, there is a short and needs to be left off)

Compressors internal overload switch- If the compressor is running when the fan motor is not, it will eventually over heat which will trip the internal overload switch and shut the compressor off until it cools back down. The best way to check this is to feel the compressor itself and see if its extremely hot. ( An over-heated compressor can cause burns!) The other way to check it would be with a multimeter with a ohm setting to check for continuity within the compressor. You must follow the wires from the compressor to find the terminals where they are connected. Take the connections off and place your leads on the wires, you should have continuity through all three wires.

Of course there are a few more technical things you can use to trouble-shoot, but these are some of the more common problems and answers. Things like the capacitor and fan motor can be pick up by yourself from a local supply store that carries A/C supplies. The compressor has to be bought from a licensed contractor. The capacitor is basic, but the fan motor will need a fan blade puller in order to replace. Hope this helps or at least points you in the right direction. Good Luck!


7/17/2010 2:46:05 AM • Goodman... • Answered on Jul 17, 2010
0helpful
1answer

My Central air unit wont cool:

it my kick out on low pressure. low on freon or 410a . over the winter monthr if the service are not tru-blued or sealing compound the systen will leak out
6/13/2010 3:44:46 PM • Goodman... • Answered on Jun 13, 2010
0helpful
1answer

My goodman cpke30-18 heat pump fan is squeaking

I would just go ahead and replace it. If you oil it, it should be done with SAE 20 wt non-detergent type oil. No WD-40!!
Hope this helps.
6/13/2010 2:12:50 AM • Goodman... • Answered on Jun 13, 2010
0helpful
1answer

Goodman cpl-j42-1a a/c unit, fan on outside unit

sounds like you have a bad fan motor in outdoor unit or a bad run capacitor ck cap first you can go 1 size larger than listed on motor data plate
6/11/2010 2:40:57 PM • Goodman... • Answered on Jun 11, 2010
0helpful
1answer

Goodman a/c j41 fan not running, turned off and on

First you need to disconnect all power. Try spinning the fan blade, if it spins freely, then try moving the shaft from side to side to see if there's any side play. If not then the bearings are OK. If there seems to be some drag when your spinning the blade, then the bearings are bad and the motor needs replaced. Then you need to have the capacitor checked, a lot of times your parts house will check it for you. If those are OK, then very carefully turn the power back on and check to see if you are getting the proper voltage to the motor terminals. if you have the proper volts and every thing checks OK, then, you need to replace the motor.
6/11/2010 2:01:55 AM • Goodman... • Answered on Jun 11, 2010
0helpful
1answer

Freezing Goodman pipes

make sure the filter is clean. also the evap coil should be clean. if none of these then your system is probably low on charge. hope this helps
6/5/2010 8:39:56 PM • Goodman... • Answered on Jun 05, 2010
0helpful
2answers

WHERE IS THE FAN CAPACITOR LOCATED

If you are talking about the outdoor unit, you need to remove the cover where the power goes in to the unit. The capacitor will be located in there along with the contactor and control board. There may be 2 seperate capacitors, 1 for the fan and 1 for the compressor but usually it's just 1 with 3 terminals on top. Com, Herm, & Fan. If you have the 3 terminal type then it is important to get the wires back in the right spot. Hope this helps.
6/2/2010 2:12:07 PM • Goodman... • Answered on Jun 02, 2010
0helpful
1answer

Third control board has been installed on a

Temporarily jump out roll out switch.
6/2/2010 3:21:33 AM • Goodman... • Answered on Jun 02, 2010
0helpful
1answer

Inside fan not turning on, outside unit is turning on

First turn the power off and see if the fan is rotates freely. Turn it by the shaft and not the fan blades. Its easier to feel the resistance. Next check you capacitor. If that's good then check the fan windings for continuity.
5/29/2010 3:28:56 PM • Goodman... • Answered on May 29, 2010
0helpful
1answer

Schrader valve extremely slight leak

No I don't think it will. They make a tool however that will allow you to change the schrader valve core without losing any charge. You can get them at HVAC supply stores. ($30+)
5/26/2010 11:39:27 PM • Goodman... • Answered on May 26, 2010
0helpful
1answer

I am looking for how many tons of cooling my

  • Here's the data you requested:
  • Goodman CKL42AR42 Split System Air Conditioner
  • Type: Split System
  • Cooling Capacity: 40000 BTU/hr (3.3 tons)
  • Energy Efficiency Rating: 9 EER
3/19/2010 5:21:55 PM • Goodman... • Answered on Mar 19, 2010
0helpful
1answer

I have 60 amp circuit breaker on my electrical a/c

You're unit is a 31/2 ton according to the numbers.Normally, breakers will only be in a half way posistion when tripped. Yes, under most conditions, the fuse will blow before the breaker trips. I have seen this many times, the breaker may be weak, burned, loose wires and so tighten wires, check the condition of the breaker.It sounds like the breaker even though it is 60 amps, is the problem and you should replace it with out hesitating. This will solve you're problem. When you pull the breaker out, look at the metal clips that snap in on the buss bar to see if they have been overheating.And the buss bar its self. You will know. I am sure this will take care of you're problem. Good Luck,
Shastalaker7
12/7/2009 10:22:26 PM • Goodman... • Answered on Dec 07, 2009
Not finding what you are looking for?
Goodman CKL42AR42 Air Conditioner Logo

113 questions posted

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Goodman Heating & Cooling

  • Goodman Heating & Cooling

Most Popular Question

fan stopped running hot

  • Heating & Cooling
Loading...